An IF 1+1 protection system is a microwave link protection system composed of a working channel and a protection channel. IF 1+1 protection includes 1+1 HSB protection, 1+1 FD protection, and 1+1 SD protection.
IF 1+1 protection can be classified into the following modes:
Revertive
The main channel or NE clears the switching state and services are switched back to it a specified period of time after it is restored to normal. The period of time that elapses after the main channel or NE is restored and before the main channel or NE clears the switching state is called the wait to restore (WTR) time. To prevent frequent switchovers caused by unstable status of the main channel or NE, a WTR time of 5-12 minutes is recommended.
Non-revertive
The main channel or NE remains in the switching state even after being restored to normal. The standby channel or NE continues to transmit services unless another switch over occurs.
Table 1 describes the 1+1 HSB switching condition (the table below lists switching conditions in descending order of priorities ).
| Switching Condition | Description |
|---|---|
Clear switching (external switching) |
All external switching states are cleared. NOTE:
In revertive mode, services are switched back to the main NE after the switching state is cleared. |
Lockout switching (external switching) |
In any state, a switching enters the lockout state. In the lockout state, no switching occurs until the lockout switching is cleared. |
Forced switching (external switching) |
If a switching is in the lockout state, no forced switching occurs. Otherwise, the system switches services from the main board to the standby board or from the standby board to the main board according to the command. The switching then enters the forced switching state. |
The main equipment is faulty |
All external switching states are cleared. Lockout switching (external switching) In any state, a switching enters the lockout state. In the lockout state, no switching occurs until the lockout switching is cleared. Forced switching (external switching) If a switching is in the lockout state, no forced switching occurs. Otherwise, the system switches services from the main board to the standby board or from the standby board to the main board according to the command. The switching then enters the forced switching state. The main equipment is faulty. If a switching is in the lockout or forced switching state, or if the current standby equipment is faulty, no HSB switching occurs. Otherwise, the system switches services from the main board to the standby board. The switching then enters the automatic switching state. |
Reverse switching (valid only when the reverse switching is enabled) |
When both the main IF board and the standby IF board at the sink end report service alarms, they send the alarms to the source end by using the MWRDI overhead in the microwave frame. If the source end is in the lockout of protection or forced switching state, or if the current standby device is faulty, reverse switching does not occur. In other cases, HSB switching occurs at the source end after the reverse switching timer expires. The reverse switching timer restarts after you successfully add a protection group or if an HSB switching event occurs. The timer duration is the wait-to-restore (WTR) time (in revertive mode) or 5 minutes (in non-revertive mode). After the reverse switching, the system changes to the RDI state. |
Manual switching (external switching) |
If a switching is in the lockout or forced switching state, or if the current standby equipment is faulty, no switching occurs. Otherwise, the system switches services from the main board to the standby board or from the standby board to the main board according to the command. The switching then enters the manual switching state. |
Revertive switching (valid only in the revertive mode) |
When the switching is in the automatic switching state and the former main equipment is already restored to normal for a period lasting for the WTR time, the revertive switching occurs. From the time the former main equipment is restored to normal to the time the revertive switching occurs, the switching is in the WTR state. After the revertive switching, the switching enters the normal state. |
Services are interrupted during HSB switching.
| Switching Type | Description |
|---|---|
Automatic switching |
The automatic switching refers to the HSM switching that is automatically triggered. After the automatic switching, the IF board receives the baseband signal sent from its paired IF board. |
Revertive switching |
After an automatic HSM switching, the IF board attempts to perform a revertive switching action periodically. If there is no service alarm on the working channel at this time, the IF board releases the switching. |
Forced switching |
The forced switching refers to the HSM switching that occurs at the same time the HSB switching occurs. After the forced switching, the IF board receives its own baseband signal. |
The 1+1 HSB and 1+1 SD modes support HSM switching.
Table 3 describes the system configuration scenarios and switching principles of IF 1+1 protection.
Protection Type |
System Configuration Scenario |
Switching Principle |
|---|---|---|
1+1 HSB |
|
|
1+1 FD |
|
|
1+1 SD |
|
|
Table 4 describes the feature dependencies and limitations of If 1+1 protection.
Feature |
Self Limitations |
Dependencies and Limitations on Other Features |
|---|---|---|
1+1 HSB |
Mix of different board types: If an ISV3 board and an ISX2/ISU2 board form a 1+1 HSB protection group, the ISV3 board must work in IS2 mode. |
|
1+1 FD |
|
|
1+1 SD |
|